    Yes. In a nutshell it's "if you don't know about electric cars, here's some information you probably don't know as well"

  • could this be an article instead of a video? I'm not spending 32 minutes watching this, tbh

    This is how I feel about any video longer than a short gif

  • This post did not contain any content.

    Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    A 240V 20amp circuit I think would meet the needs of 99% of commuters in the US. If your average miles/kWh is around 3.3 and you're charging at 80% of the 20amp breaker limit (as you should be), even factoring in 10% losses in power transmission, you're still charging somewhere around 11 miles per hour. Easy 100+ miles overnight with zero infrastructure change outside of a couple wire nuts and a cheap charger. Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier...

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    Running more than one outlet on a 220 circute is generally against us codes. It will work but don't do it.

    I have a phev with only 30 miles of range - ofen I get home with a nearly dead battery and need to leave again soon - I want faster charging. I'm sure someone with 200 miles of range can be fine on 110 volt slow charging as there likely enough time over a week that it works.

  • This post did not contain any content.

    I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

  • This post did not contain any content.

    Yeah I don’t need to refill my battery in 2 hours, but it’s nice to be able to meaningfully top off between errands to make the most of a small PHEV battery.

  • This post did not contain any content.

    I agree with this youtube comment:

    As an electrician (in Australia), I agree with your basic premise. However, if you are asking me to install an EV charger, unless you tell me “I want it to charge slowly with a limited current capacity”, I am going to assume it is to charge an EV under ALL situations - fast to slow, for whoever may drive one today or in the future, even with a potential new homeowner. We generally do our work with the priority order (1) safety - nobody gets an electric shock and nothing catches fire; (2) avoidance of nuisance i.e. the thing you just installed doesn’t work and keeps tripping the breaker 😑 (3) avoiding needing replacement electrical work for at least 25 - 50 years

    Also I live in a townhouse with no garage. Our charger is between the neighborhood sidewalk and our parking spaces, so I'd prefer keeping it plugged in as little as possible to minimize any issues with foot traffic (neighbors, delivery people, garbage pickup, etc). I've seen other townhouse EV owners literally run an extension cable over the sidewalk to do an L1 charge for their EV and that's just asking for trouble.

  • Running more than one outlet on a 220 circute is generally against us codes. It will work but don't do it.

    I have a phev with only 30 miles of range - ofen I get home with a nearly dead battery and need to leave again soon - I want faster charging. I'm sure someone with 200 miles of range can be fine on 110 volt slow charging as there likely enough time over a week that it works.

    I think #1 is suggesting to move the neutral over to another hot phase and change the outlet to a 240v nema 6/three prong (I think) with two hots and a ground instead of the 4 prong.

    The 240v at the same amps gives you higher watts so faster charging without an expensive new conductor. I'm

  • I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

    What kind of range do you have on that? I've been debating installing a l2 charger because overnight charging is usually good enough. I tend to get about 15-20 miles range tops on pure electric.

  • I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

    Yep the difference for our setup was going from 12-18 hour full charge times (Level 1) to about 6 hours on Level 2. L1 charger could only put out 12 amps at 120v, and while the L2 charger can do up to 50A of 240v power, our vehicle can only use about a third of that capacity at max draw.

    So as the video's topic covers, we didn't need a 50A circuit for Level 2 charging on our limited vehicle. But I put in a full 50A circuit anyway so now I can eventually upgrade our other car to electric or PHEV and be ready for whatever those need.

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    If your home ever suffered an electrical fire then this sort of jury rigging is precisely the sort of thing any competent insurance inspector would spot, and insurance carriers would deny coverage for since it clearly isn’t code compliant, which means a licensed electrician didn’t install it and it wasn’t properly inspected.

  • I think #1 is suggesting to move the neutral over to another hot phase and change the outlet to a 240v nema 6/three prong (I think) with two hots and a ground instead of the 4 prong.

    The 240v at the same amps gives you higher watts so faster charging without an expensive new conductor. I'm

    The problem with #1 is that most garages only have one circuit for the outlets AND the garage door opener. Moving to 240v would fry the opener.

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    If your home ever suffered an electrical fire then this sort of jury rigging is precisely the sort of thing any competent insurance inspector would spot, and insurance carriers would deny coverage for since it clearly isn’t code compliant, which means a licensed electrician didn’t install it and it wasn’t properly inspected.

  • I think #1 is suggesting to move the neutral over to another hot phase and change the outlet to a 240v nema 6/three prong (I think) with two hots and a ground instead of the 4 prong.

    The 240v at the same amps gives you higher watts so faster charging without an expensive new conductor. I'm

    Changing a 120v line over to 240 is likely also against code even if the physical cable can handle it. 120V cable is typically white/black/green, and the electrical code prohibits using the white one as a hot leg. That’s why 240V cable of the same AWG is red/black/green. The red & black legs both carry 120V.

  • You should give it a shot. The dudes videos are super captivating.

    For me, they're captivating for about 5 minutes. Then the dry humor and constant cries of outrage become irritating. He could probably make 15-20 minute, info-dense videos without all the extra "personality".

  • #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    If your home ever suffered an electrical fire then this sort of jury rigging is precisely the sort of thing any competent insurance inspector would spot, and insurance carriers would deny coverage for since it clearly isn’t code compliant, which means a licensed electrician didn’t install it and it wasn’t properly inspected.

    #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    I'll be the first to admit I'm no certified Sparky, but wire relabeling is used in a number of situations fully in accordance with NEC. My understanding is that some of this is in NEC 200.7. It requires relabeling both ends, but I don't think there's any code violation with it. If what you're saying was true, wouldn't that mean any -2 NM (Romex) would be code incompatible with 240v loads? I don't think that's true.

    Edit: here's a Sparky doing exactly that

  • A 240V 20amp circuit I think would meet the needs of 99% of commuters in the US. If your average miles/kWh is around 3.3 and you're charging at 80% of the 20amp breaker limit (as you should be), even factoring in 10% losses in power transmission, you're still charging somewhere around 11 miles per hour. Easy 100+ miles overnight with zero infrastructure change outside of a couple wire nuts and a cheap charger. Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier...

    Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier…

    If you do a receptacle, you've got to then do a GFCI. Check out the price difference between a GFCI breaker and one that isn't. If you hardware the EVSE, you don't need GFCI because GFCI is built into nearly all EVSE. If we're doing this exercise to keep low costs, adding GFCI outside of the EVSE jacks up the price.

  • What kind of range do you have on that? I've been debating installing a l2 charger because overnight charging is usually good enough. I tend to get about 15-20 miles range tops on pure electric.

    30-35 miles, depending on the season.

  • I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

    Agreed, and that headline is needlessly inflammatory . Looking at my EV mileage , I could almost certainly get away with just plugging into a standard outlet. However the level 2 charger means that even if I screw it up, I can be mostly charged in a couple of hours. It’s been really effective at helping me get over what range anxiety I had. It’s really helped keep car usage as a somewhat impulse thing, rather than a process: I’m ready to go anywhere anytime.

    It also means I can charge multiple EVs, if I wanted to.

  • Large Language Model Performance Doubles Every 7 Months

    Technology technology
    53
    1
    100 Stimmen
    53 Beiträge
    137 Aufrufe
    V
    in yes/no type questions, 50% success rate is the absolute worst one can do. Any worse and you're just giving an inverted correct answer more than half the time
  • 31 Stimmen
    1 Beiträge
    1 Aufrufe
    Niemand hat geantwortet
  • 129 Stimmen
    22 Beiträge
    71 Aufrufe
    N
    I can’t believe he knows anybody like that. You think you know somebody…
  • 48 Stimmen
    19 Beiträge
    71 Aufrufe
    mrjgyfly@lemmy.worldM
    Does that run the risk of leading to a future collapse of certain businesses, especially if their expenses remain consistently astronomical like OpenAI? Please note I don’t actually know—not trying to be cheeky with this question. Genuinely curious.
  • Fake It Till You Make It? Builder.ai’s $1.5B AI Scam Exposed

    Technology technology
    14
    1
    70 Stimmen
    14 Beiträge
    44 Aufrufe
    W
    Religion and fiat are always at the top
  • AI cheating surge pushes schools into chaos

    Technology technology
    25
    45 Stimmen
    25 Beiträge
    91 Aufrufe
    C
    Sorry for the late reply, I had to sit and think on this one for a little bit. I think there are would be a few things going on when it comes to designing a course to teach critical thinking, nuances, and originality; and they each have their own requirements. For critical thinking: The main goal is to provide students with a toolbelt for solving various problems. Then instilling the habit of always asking "does this match the expected outcome? What was I expecting?". So usually courses will be setup so students learn about a tool, practice using the tool, then have a culminating assignment on using all the tools. Ideally, the problems students face at the end require multiple tools to solve. Nuance mainly naturally comes with exposure to the material from a professional - The way a mechanical engineer may describe building a desk will probably differ greatly compared to a fantasy author. You can also explain definitions and industry standards; but thats really dry. So I try to teach nuances via definitions by mixing in the weird nuances as much as possible with jokes. Then for originality; I've realized I dont actually look for an original idea; but something creative. In a classroom setting, you're usually learning new things about a subject so a student's knowledge of that space is usually very limited. Thus, an idea that they've never heard about may be original to them, but common for an industry expert. For teaching originality creativity, I usually provide time to be creative & think, and provide open ended questions as prompts to explore ideas. My courses that require originality usually have it as a part of the culminating assignment at the end where they can apply their knowledge. I'll also add in time where students can come to me with preliminary ideas and I can provide feedback on whether or not it passes the creative threshold. Not all ideas are original, but I sometimes give a bit of slack if its creative enough. The amount of course overhauling to get around AI really depends on the material being taught. For example, in programming - you teach critical thinking by always testing your code, even with parameters that don't make sense. For example: Try to add 123 + "skibbidy", and see what the program does.
  • 4 Stimmen
    12 Beiträge
    18 Aufrufe
    guydudeman@lemmy.worldG
    Yeah, I don’t know how they’re doing it. They’re using some “zero trust” system. It’s beyond me.
  • 0 Stimmen
    6 Beiträge
    27 Aufrufe
    P
    Outlook.... Ok Pretty solid Bahaha hahahahaha Sorry. Outlook is a lot of things. "Gooey crap" would be one way to describe it, but "solid"? Yeah, no. Gmail is (well, was) pretty solid. There are a lot of other webmail providers out there, including self hosted options and most are pretty solid, yeah. Outlook, though? It's a shit show, it's annoying. Do you love me? Please love me, please give feedback, please give feedback again, please look at this, hey am I the best? Am I.. STFU YOU PIECE OF CRAP! Can you PLEASE just let me do my email without being an attention whore every hour? Even down to the basics. Back button? "What is that? Never heard of it, can't go back to the message I just was on because I'm Microsoft software and so half baked." Having two tabs open? "Oh noes, now I get scawed, now I don't know how to manage sessions anymore, better just sign you out everywhere." What is it with Microsoft and not being able to do something basic as sessions normal? I'm not even asking for good, definitely not "awesome", just normal, and that is already too much to ask. Try running it in Firefox! I'm sure it's totally not on purpose, just "oopsie woopsie poopsie" accidentally bwoken. Maybe it's working again today, who knows, tomorrow it'll be broken again. I run everything on Firefox except the Microsoft sites, they have to be in chrome because fuck you, that's why. Seriously, I can't take any Microsoft software seriously at this point, and all of it is on its way out in our company, I'm making sure of that