    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    A 240V 20amp circuit I think would meet the needs of 99% of commuters in the US. If your average miles/kWh is around 3.3 and you're charging at 80% of the 20amp breaker limit (as you should be), even factoring in 10% losses in power transmission, you're still charging somewhere around 11 miles per hour. Easy 100+ miles overnight with zero infrastructure change outside of a couple wire nuts and a cheap charger. Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier...

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    Running more than one outlet on a 220 circute is generally against us codes. It will work but don't do it.

    I have a phev with only 30 miles of range - ofen I get home with a nearly dead battery and need to leave again soon - I want faster charging. I'm sure someone with 200 miles of range can be fine on 110 volt slow charging as there likely enough time over a week that it works.

  • This post did not contain any content.

    I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

  • This post did not contain any content.

    Yeah I don’t need to refill my battery in 2 hours, but it’s nice to be able to meaningfully top off between errands to make the most of a small PHEV battery.

  • This post did not contain any content.

    I agree with this youtube comment:

    As an electrician (in Australia), I agree with your basic premise. However, if you are asking me to install an EV charger, unless you tell me “I want it to charge slowly with a limited current capacity”, I am going to assume it is to charge an EV under ALL situations - fast to slow, for whoever may drive one today or in the future, even with a potential new homeowner. We generally do our work with the priority order (1) safety - nobody gets an electric shock and nothing catches fire; (2) avoidance of nuisance i.e. the thing you just installed doesn’t work and keeps tripping the breaker 😑 (3) avoiding needing replacement electrical work for at least 25 - 50 years

    Also I live in a townhouse with no garage. Our charger is between the neighborhood sidewalk and our parking spaces, so I'd prefer keeping it plugged in as little as possible to minimize any issues with foot traffic (neighbors, delivery people, garbage pickup, etc). I've seen other townhouse EV owners literally run an extension cable over the sidewalk to do an L1 charge for their EV and that's just asking for trouble.

  • Running more than one outlet on a 220 circute is generally against us codes. It will work but don't do it.

    I have a phev with only 30 miles of range - ofen I get home with a nearly dead battery and need to leave again soon - I want faster charging. I'm sure someone with 200 miles of range can be fine on 110 volt slow charging as there likely enough time over a week that it works.

    I think #1 is suggesting to move the neutral over to another hot phase and change the outlet to a 240v nema 6/three prong (I think) with two hots and a ground instead of the 4 prong.

    The 240v at the same amps gives you higher watts so faster charging without an expensive new conductor. I'm

  • I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

    What kind of range do you have on that? I've been debating installing a l2 charger because overnight charging is usually good enough. I tend to get about 15-20 miles range tops on pure electric.

  • I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

    Yep the difference for our setup was going from 12-18 hour full charge times (Level 1) to about 6 hours on Level 2. L1 charger could only put out 12 amps at 120v, and while the L2 charger can do up to 50A of 240v power, our vehicle can only use about a third of that capacity at max draw.

    So as the video's topic covers, we didn't need a 50A circuit for Level 2 charging on our limited vehicle. But I put in a full 50A circuit anyway so now I can eventually upgrade our other car to electric or PHEV and be ready for whatever those need.

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    If your home ever suffered an electrical fire then this sort of jury rigging is precisely the sort of thing any competent insurance inspector would spot, and insurance carriers would deny coverage for since it clearly isn’t code compliant, which means a licensed electrician didn’t install it and it wasn’t properly inspected.

  • I think #1 is suggesting to move the neutral over to another hot phase and change the outlet to a 240v nema 6/three prong (I think) with two hots and a ground instead of the 4 prong.

    The 240v at the same amps gives you higher watts so faster charging without an expensive new conductor. I'm

    The problem with #1 is that most garages only have one circuit for the outlets AND the garage door opener. Moving to 240v would fry the opener.

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    If your home ever suffered an electrical fire then this sort of jury rigging is precisely the sort of thing any competent insurance inspector would spot, and insurance carriers would deny coverage for since it clearly isn’t code compliant, which means a licensed electrician didn’t install it and it wasn’t properly inspected.

  • I think #1 is suggesting to move the neutral over to another hot phase and change the outlet to a 240v nema 6/three prong (I think) with two hots and a ground instead of the 4 prong.

    The 240v at the same amps gives you higher watts so faster charging without an expensive new conductor. I'm

    Changing a 120v line over to 240 is likely also against code even if the physical cable can handle it. 120V cable is typically white/black/green, and the electrical code prohibits using the white one as a hot leg. That’s why 240V cable of the same AWG is red/black/green. The red & black legs both carry 120V.

  • You should give it a shot. The dudes videos are super captivating.

    For me, they're captivating for about 5 minutes. Then the dry humor and constant cries of outrage become irritating. He could probably make 15-20 minute, info-dense videos without all the extra "personality".

  • #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    If your home ever suffered an electrical fire then this sort of jury rigging is precisely the sort of thing any competent insurance inspector would spot, and insurance carriers would deny coverage for since it clearly isn’t code compliant, which means a licensed electrician didn’t install it and it wasn’t properly inspected.

    #1 is a terrible idea if you ever need to hire an electrician in the future, plan on selling your house, etc. The National Electric Code prohibits using white, green, or grey wire for a hot/load connection. The 120V cable will contain a black wire for the hot connection, white for neutral, and green for ground. To properly convert it to 240V you would need a cable that consists of black & red wires for the two 120V legs.

    I'll be the first to admit I'm no certified Sparky, but wire relabeling is used in a number of situations fully in accordance with NEC. My understanding is that some of this is in NEC 200.7. It requires relabeling both ends, but I don't think there's any code violation with it. If what you're saying was true, wouldn't that mean any -2 NM (Romex) would be code incompatible with 240v loads? I don't think that's true.

    Edit: here's a Sparky doing exactly that

  • A 240V 20amp circuit I think would meet the needs of 99% of commuters in the US. If your average miles/kWh is around 3.3 and you're charging at 80% of the 20amp breaker limit (as you should be), even factoring in 10% losses in power transmission, you're still charging somewhere around 11 miles per hour. Easy 100+ miles overnight with zero infrastructure change outside of a couple wire nuts and a cheap charger. Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier...

    Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier…

    If you do a receptacle, you've got to then do a GFCI. Check out the price difference between a GFCI breaker and one that isn't. If you hardware the EVSE, you don't need GFCI because GFCI is built into nearly all EVSE. If we're doing this exercise to keep low costs, adding GFCI outside of the EVSE jacks up the price.

  • What kind of range do you have on that? I've been debating installing a l2 charger because overnight charging is usually good enough. I tend to get about 15-20 miles range tops on pure electric.

    30-35 miles, depending on the season.

  • I think “might be overkill” would be a better title and position than “usually overkill.”

    There is absolutely a subset of EV drivers that could get by with a level 1 charger (ignoring time of day rates), but most people would fall behind anytime they drive further than the average number of miles. Sure, taking 10 hours to recharge your Chevy Bolt overnight when you’ve driven 40 miles is doable; 64 hours when you’ve returned home from a longer trip isn’t.

    I own a PHEV, and installing a level 2 charge has been one of the best quality of life and financial changes.

    Agreed, and that headline is needlessly inflammatory . Looking at my EV mileage , I could almost certainly get away with just plugging into a standard outlet. However the level 2 charger means that even if I screw it up, I can be mostly charged in a couple of hours. It’s been really effective at helping me get over what range anxiety I had. It’s really helped keep car usage as a somewhat impulse thing, rather than a process: I’m ready to go anywhere anytime.

    It also means I can charge multiple EVs, if I wanted to.

  • What kind of range do you have on that? I've been debating installing a l2 charger because overnight charging is usually good enough. I tend to get about 15-20 miles range tops on pure electric.

    The way I explained it to my brother:

    • technically just plug in to an existing outlet will work. Even if you didn’t keep up every day, you would get tot the weekend and make it up then
    • but your garage already has a dryer outlet. Adapters are cheap and it will charge 4-5 times as fast
    • but 50a level 2 charger is the same size as a stove outlet. Maybe a little longer wire run, and the “outlet” is more expensive, but it’s well worth the cost for the freedom, the flexibility, the convenience … and may even add to your house value
  • Hell, depending on local codes, you might get away with slapping in a nema 6-20 receptacle to make it even easier…

    If you do a receptacle, you've got to then do a GFCI. Check out the price difference between a GFCI breaker and one that isn't. If you hardware the EVSE, you don't need GFCI because GFCI is built into nearly all EVSE. If we're doing this exercise to keep low costs, adding GFCI outside of the EVSE jacks up the price.

    Fair enough! Anyone with existing 240v receptacles of any kind is a lucky duck, regardless.

  • Good video. Accurate information.

    Two notes:

    1. For North American homes: I agree with the overlooked value of a downrated circuit for EV charging, but I don't think he talked about a possibly better option for downrating: Using an existing 120v circuit (at whatever current rating) already wired in the garage . Remove the outlet, install EVSE (charger), and swap the breaker for a 240v one (at a current rating matching the original. So if you have a 120v 15A circuit (white romex) you can use the exact same wire for a 240v at 15A. If you have a 20A (yellow romex) you would end up with a 240v 20A. You get more than double the speed of charging with zero new wires added, only changing the breaker and removing the old outlets. Note: If you have multiple outlets in your garage all fed from this same circuit, this would mean all of your outlets in the garage are now 240v and not usable for regular 120v items.

    2. He didn't like Smart chargers. Thats a valid opinion, but smart chargers can do some nice things that I like. Some will also talk to each other if you have two chargers, such as if you have two EVs. They can be configured to share the same wire to the breaker box, so you can plug both cars in at night, one car will charge, then when that is complete, the other will charge automatically without having to unplug one car and then plug in the other. It will charge the least charged car first ensuring the best balance of charge to both cars assuming both cars can't be charged to full in one night. If you have solar panels, some smart chargers can talk to the solar system and be instructed to only charge when there is excess power that would otherwise go to waste. It can do this automatically so if clouds go overhead and not enough juice is available from the sun, the charging stops. As soon as the clouds clear and there is an excess again, charging resumes automatically. For outdoor charging, you can also configure most Smart chargers to only charge you authorized cars. So you don't need to worry about someone rolling into your driveway when you're not home (or a bad neighbor) and running up your electricity bill.

    For me the smart charger was a key feature, and I never understood why that is never talked about. I have 200a service which was plenty for one fully powered charging service, but with the likelihood of electrification in upcoming years I was hesitant to have two. It was pretty clear I needed to prioritize smart charging so I’d have that possibility.

    I can also configure it to only charge my allowed vehicles, should that ever become an issue

    So far my family only has the one EV, so we only need the one charger. But I like that if we needed a second charger it could be on the same circuit and they could dynamically share the power to maximize charging

  • Financial 'stretch' for UK to join Europe's Starlink rival

    Technology technology
    1
    1
    27 Stimmen
    1 Beiträge
    1 Aufrufe
    Niemand hat geantwortet
  • Tech support 'trained monkey’ fixed problem with two fingers

    Technology technology
    7
    1
    31 Stimmen
    7 Beiträge
    1 Aufrufe
    S
    I can understand why some programs only allow a single copy to be opened at once, something like email makes sense. However on Linux they got this right... if you try to open a program that is already running, it switches to the screen that program is on and restores the program window to the desktop. There's no guessing why the program "won't open", it just makes the logical choice that you want to see it. Heh that reminds me of another detail from that call... the guy also wasn't willing to reboot his computer (which would have solved the problem as well), but berated me for not knowing what I was doing for making the suggestion. Dude, it's Windows, things break constantly and a reboot generally resolves the issue.
  • AI Leaves Digital Fingerprints in 13.5% of Scientific Papers

    Technology technology
    2
    1
    158 Stimmen
    2 Beiträge
    2 Aufrufe
    F
    So they established that language patterns measured by word frequency changed between 2022 and 2024. But did they also analyse frequencies across other 2-year time periods? How much difference is there for a typical word? It looks like they have a per-frequency significance threshold but then analysed all words at once, meaning that random noise would turn up a bunch of "significant" results. Maybe this is addressed in the original paper which is not linked.
  • Lighter, Stronger, Smarter: The Rise of Syntactic Foams

    Technology technology
    1
    1
    0 Stimmen
    1 Beiträge
    9 Aufrufe
    Niemand hat geantwortet
  • CBDC Explained : Can your money really expire?

    Technology technology
    4
    6 Stimmen
    4 Beiträge
    23 Aufrufe
    S
    CBDCs could well take the prize for most dangerous thing in our lifetime, similar to nuclear weapons during the Cold War. I'm thinking of that line from the song in Les Mis. Look down, look down. You'll always be a slave. Look down, look down. You're standing in your grave.
  • Amazon is reportedly training humanoid robots to deliver packages

    Technology technology
    143
    1
    300 Stimmen
    143 Beiträge
    234 Aufrufe
    M
    Yup, and people seem to frequently underestimate how ridiculously expensive running a fleet of humanoid robots would be (and don’t seem to realize how comparatively low the manual labor it’d replace is paid.)
  • 17 Stimmen
    1 Beiträge
    11 Aufrufe
    Niemand hat geantwortet
  • AI cheating surge pushes schools into chaos

    Technology technology
    25
    45 Stimmen
    25 Beiträge
    91 Aufrufe
    C
    Sorry for the late reply, I had to sit and think on this one for a little bit. I think there are would be a few things going on when it comes to designing a course to teach critical thinking, nuances, and originality; and they each have their own requirements. For critical thinking: The main goal is to provide students with a toolbelt for solving various problems. Then instilling the habit of always asking "does this match the expected outcome? What was I expecting?". So usually courses will be setup so students learn about a tool, practice using the tool, then have a culminating assignment on using all the tools. Ideally, the problems students face at the end require multiple tools to solve. Nuance mainly naturally comes with exposure to the material from a professional - The way a mechanical engineer may describe building a desk will probably differ greatly compared to a fantasy author. You can also explain definitions and industry standards; but thats really dry. So I try to teach nuances via definitions by mixing in the weird nuances as much as possible with jokes. Then for originality; I've realized I dont actually look for an original idea; but something creative. In a classroom setting, you're usually learning new things about a subject so a student's knowledge of that space is usually very limited. Thus, an idea that they've never heard about may be original to them, but common for an industry expert. For teaching originality creativity, I usually provide time to be creative & think, and provide open ended questions as prompts to explore ideas. My courses that require originality usually have it as a part of the culminating assignment at the end where they can apply their knowledge. I'll also add in time where students can come to me with preliminary ideas and I can provide feedback on whether or not it passes the creative threshold. Not all ideas are original, but I sometimes give a bit of slack if its creative enough. The amount of course overhauling to get around AI really depends on the material being taught. For example, in programming - you teach critical thinking by always testing your code, even with parameters that don't make sense. For example: Try to add 123 + "skibbidy", and see what the program does.